[Comtec Announce] [Core Network] Service Alert 17th July 2014 - Update 2

David Croft david at comtec.net.uk
Thu Jul 17 14:39:59 BST 2014


This is an incident notification regarding our core network at
Interxion LON1 (Site CLBIS02).

Date: Monday, 9th June 2014
Start time: 13:54
End time: 14:18

Services affected:

Core Network
Services single-homed out of Interxion LON1 (CLBIS02).

Report:

We observed a large increase in temperature over a short time window.
The data centre dispatched engineers to investigate and the
temperature quickly dropped again.

A service alert was issued at 14:08 to warn customers of the
possibility of a short-notice shutdown to prevent equipment damage.
However, no shutdown was necessary and no services were impacted.

The probable cause appears to have been other customers working nearby
placing equipment in front of our rack and blocking airflow.

We have asked the data centre to install additional ventilation floor
tiles in front of our rack to prevent this issue happening again and
will follow up to ensure that this work is completed.

This is the final update.

Comtec NOC was tracking this issue under ticket [#BHC-445-92607].